FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Problem with Fan Power input for System 6

Dear Experts, I am straggling to input Fan Power in the baseline model (System 6 - Packaged VAV with PFP Boxes) and have the following issues: 1- In Table 1.4.6 - General HVAC, there is a note for this type of system that requires “All Baseline fans in parallel VAV fan-powered boxes sized for 50% of peak primary airflow and modeled with 0.35 W/cfm fan power and a minimum flow setpoint of 30% of peak (or minimum ventilation rate) per G3.1.3.14”. Supply and return air of the system are equal, 49,202 cfm for each. Based on this cfm, supply fan power and return fan power is 17.22 KW (49,202 * 0.35). This number is different with the figure from ASHRAE 90.1-2007 Baseline Fan Power Calculator (The spreadsheet from 7group). In addition, when I input the supply and return cfm and 17.22 KW for both fans in “Table 1.4.7A - Baseline Air-Side HVAC System Schedule”, it indicates “Allowed Fan Power” to be 55.4 KW and it would be red marked with any other numbers input as system fan power. 2- In eQUEST’s “Fan Power and Control” screen, the input boxes for supply and return design KW/cfm are grayed out (n/) and I cannot input any data for the fan powers. I would truly appreciate your comments, Morteza

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/17/2013 - 14:21

1 - The 0.35 W/cfm is in addition to the system fan power calculated under G3.1.2.9. This value is determined at each individual box based on its air flow. The spreadsheet only calculates the G3.1.2.9 baseline fan power for the major system fans and does not include the fan-powered boxes. Table 1.4.7A will only accurately calculate the baseline fan power if you enter each individual baseline system in a separate column. If you add everything up and put it in one column the baseline fan power will calculate slightly lower than the total of each system individually. 2 - Are you sure you have entered the correct baseline system? That is the only reason we can think of for the boxes being grayed out.