FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Primary Secondary Pumping Power

When modeling a project that has a baseline building requiring system #8, the system cooling tonnage is > 600 tons therefore G3.1.3.10. calls for a primary/secondary pumping loop served by two equally sized chillers. The baseline was modeled with 22W/gpm pump power for the primary chiller pumps (1 pump per chiller, two chillers total) and secondary chilled water loop pump (1 pump). A LEED reviewer has commented that the baseline should have been modeled with total primary/secondary loop pump power of 22W/gpm. Please clarify if the baseline was modeled correctly considering the first line of G3.1.3.10 states "The baseline building design pump power shall be 22 W/gpm."

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/06/2013 - 18:56

An ASHRAE interpretation IC 90.1-2007-14 has clarified this issue. The 22 W/gpm is for all the chilled water pumps combined, not for each one.