FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Pressure Drop Adjustment

We are working on a Project with a central 100%OA AHU. We calculated the pressure drop adjustment for the baseline Systems 7 following ASHRAE 90.1-2007 table G3.1.2.9. Now we received the following review comment: "The Baseline fan power calculations indicate that a pressure drop adjustment factor has been applied to the total supply air volume of each system in the Baseline model to reflect the high efficiency filters included in the actual design; however, the high efficiency filters only filter the outdoor air volume provided by the dedicated outdoor air systems in the actual design. Revise the Baseline model, as needed, so the pressure drop adjustment factor associated with the high efficiency filters is applied to the total outdoor air volume only, not the total supply air volume, in the Baseline model. Further, update Table 1.4.2 and provide revised fan power calculations reflecting the changes." In our understanding, the review team wants a differentiation between OA and Return Air of System 7 for the pressure drop adjustment calculation. ASHRAE 90.1-2007 G3.1.2.9 definition for the calculation is "the baseline system maximum design supply fan airflow rate". Now it is unclear if the review team is wrong with their comment or if we have to make a differentiation of OA and return air. Any ideas? Thank you in advance!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/06/2013 - 17:04

The pressure drop adjustments only apply to the applicable air flow in the system. For example, if you have ducted returns the adjustment only applies to the the return air flow not the supply airflow. In your case if the baseline unit is 100% OA then the supply air and OA flows are the same and the PDA would be applied to the supply airflow. However, just because your proposed system is 100% OA does not necessarily make your baseline system 100% OA. The baseline supply air is auto-calculated by the software and the OA is identical to the proposed OA. So if the baseline supply air is greater than the proposed OA the baseline unit is not 100% OA. In this scenario if the filters are on the OA then only the OA flow would be used to apply the PDA. There is a spreadsheet which we created under the Documentation Toolkit above which is set up so that you can apply a portion of the air flow to an individual PDA.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.