NC-2009 SSc4.2:Alternative transportation - bicycle storage and changing rooms

In the prelimary review

In the prelimary review comments to achieve this credit we recive the next comment: "Provide supplemental calculations confirming that sufficient shower facilities have been provided to serve all FTE occupants with access to the amenities, including individuals who are not part of this LEED project." The question is how should we calculate the shower rooms, is it a formula?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/04/2014 - 16:34

Hi Jorge, This kind of comment generally indicates that you are using showers for your LEED area that are also available to others, like showers in an adjacent building. If that is the case, you need to separate the showers into a fixture group so that you can add the other FTEs that are able to use it. You would use the same 0.5% calculation with those additional FTEs as you do for the ones within your LEED boundary.