Forum discussion

NC-2009 EAc4:Enhanced refrigerant management

Phase-out Plans for conversion

I am working on an addition to an existing building, the addition is attempting certification. The exsting building and the chiller plant do comply with EAp3, but, 2 chillers are HCFC-22 and raise the ARI to above 100. In order to comply with EAc4 the 2 chillers will have to be changed over to R-407c or be replaced. Question is, will it be required to be retrofitted or replaced before construction is completed or can it be completed within a 5-year timeline? Thanks for your help. Scott

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/20/2012 - 22:47

The retrofit/replacement should be done before construction is completed. While a phase-out is allowed in the prerequisite, EAc4 is like other credits where the credit should be achieved as part of the LEED scope of work.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.