Forum discussion

NC-2009 IEQc3.2:Construction IAQ management plan - before occupancy

Option 1 Path 2 Mechanical & Electrical Rooms

I am working on a project that has multiple AHUs serving different types of spaces and we also have several large mechanical and electrical rooms. Each of the mechanical and electrical rooms have a dedicated AHU. The electrical room AHU will have both heating and cooling and the mechanical room AHU will only have heating and is used only to ventilate the mechanical room. Since these types of rooms are not "occupied" with people, do they need to be flushed-out to comply with IEQc3.2?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/20/2016 - 16:32

All occupiable (regularly/non-regularly/unoccupied) areas of the project building must be included within the flushout. Mechanical rooms that are considered to be "unoccupied" per the ventilation calculations must be included in the flush-out calculations.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.