Optimize energy on Datacenter equipments

Hello,

An office building project has a small space dedicated to a Datacenter (under 20% of GFA). It was designed to be Tier 3 certified with all the requirements that that entails. (Redundant UPS units,...)

1) Do we need to model Datacenter equipment under Unregulated Loads?

2) How would we justify an energy reduction in that specific equipment using Exception Calculation Method ?

Thank you

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/16/2018 - 17:14

1. Yes 2. There is a spreadsheet for data centers that defines the baseline and can help you to determine the savings. https://www.usgbc.org/resources/minimum-energy-performance-data-center-calculator