Forum discussion

NC-2009 IEQc6.2:Controllability of systems - thermal comfort

Operable windows

For an office space with 100 individual working spaces the project team has used operable windows in order to provide thermal comfort control. 80 working spaces are located within 20 feet of a window to the inside, and ten feet from side to side. However, we have got a response from the reviewer that “it is unclear that this space has 80 individual operable windows.” From our understanding operable windows are not supposed to be individual, which cannot occur by definition in an open-plan office space. Is that correct?

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/06/2015 - 22:09

That's a rough comment. The credit says you need to be close to an operable window OR have individual control. I'd recommend you appeal the decision if you're rejected.

Mon, 05/11/2015 - 14:41

I agree with Dylan, the review comment is incorrect.

Wed, 06/01/2016 - 13:36

Charalampos, was your approch accepted by GBCI or did they say in the end that there has to be one operable window per person in order to comply with the credit requirements?

Thu, 06/02/2016 - 07:31

Agata, just to clarify that this project was seeking the corresponding credit of v4. However, although the reviewer's technical advice is not part of the "changes from LEED 2009" section of v4 reference guide we had to comply with it and provide alternative means of the thermal comforts such as desktop fans.

Thu, 06/02/2016 - 07:46

Do you know if it's still possible to achieve this credit in v2009 by using operable windows (one window would be for more than one person or two)? People without access to windows could use fancoil units.

Thu, 06/02/2016 - 07:55

So far yes, we have managed to achieve this credit at v3 projects with one operable window for more than one occupants as long as those occupants are within 20 feet of this window to the inside, and 10 feet from side to side.

Thu, 06/02/2016 - 07:59

Thank you for a quick response!

Thu, 06/02/2016 - 21:46

Hi Charalampos, the requirement for operable windows has not changed for LEED v4. I will discuss this with GBCI to make sure it is being interpreted properly for LEED v4, and we will consider releasing an addendum to the reference guide to further clarify.

Fri, 06/03/2016 - 14:05

Thanks Larissa! That would be very helpful!

Mon, 06/27/2016 - 15:55

Hi Larissa, we've just received a review for a v2009 project and the reviewer has commented that "it appears that each operable window has been counted as a thermal control for multiple occupants located close to the windows and that this credit only allows an operable window to be utilized as a single thermal control (e.g. each operable window could only be applied to one workstation or shared multi occupant space)." Obviously so far we have been able to comply with the credit requirements providing operable windows which are not individually operable. Did you have the chance to discuss this issue with the GBCI? Thank you.

Mon, 06/27/2016 - 19:32

Hi Charalampos, Yes I have talked with GBCI about this issue for LEED 2009 and LEED v4. They will be clarifying the requirements to the reviewers but there may be a few projects already in the pipeline that will be impacted as your project apparently has. Thanks!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.