Forum discussion

CS-2009 IEQp1:Minimum indoor air quality performance

Occupant Default Density vs. Actual density

Hello, we are working on a C&S Mall project, is it permitted that we uncheck the Default density checkbox in IEQp1 form, and enter expected number of persons based on Architects / Engineers expected densities, which are lower than the ASHRAE 62.1-2007 default density? If yes, is a justification from the Architects / Engineers is enough based on available parking spaces + maximum other mall visitors + previous projects in the country? Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 10/09/2015 - 12:56

The reference states "project that do have tenant occupancy counts must use these numbers as long as the gross square footage per occupant is not greater than the that in the default occupant density in Table 6.1"

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.