We are working on getting an 8-story office building LEED EBOM certified. The system utilizes large built up air handlers to provide supply air to fan powered VAV boxes. The system is designed for full economizer when the ambient air conditions are sufficient. During occupied hours approximately 20% outside air is being provided through the outside air louver most of the time, but when ambient temperature is below 35 degF and above 85 degF the outside air damper closes because the building cannot maintain temperature set point. We have louver, fan, duct, ect. capacity to meet 62.1 flow rates, but the system cannot maintain set point at the mentioned ambient conditions.

It seems that meeting ASHRAE standard 62.1-2007 is infeasible because of physical constraints limiting the system to provide outside air when outside air is below 35 degF and above 85 degF. Therefore, I assume that we would pursue case 2 and provide 10 cfm of outside air per person. Case 2 states that we need to demonstrate that the current system cannot provide 62.1 outside air flow rates “under any operating condition even when functioning properly”.

My question is since we can provide the required outside air most of the time, does that mean we don’t meet the requirements of case 2 and are out of luck? Thank you for any help that you can provide!