Forum discussion

NC-v4 EAp2:Minimum energy performance

OA in baseline model for residential building

Hello,

I am modeling a 40-story residential building located in Miami and I am following the Energy star “Multifamily high rise program, Version 1.0, Revision 03” simulation guidelines. The designed outdoor air rate is 60% higher than the OA required by ASHRAE 62.1 2010.

The guideline specifies:

“3.12.2.2 Whole-unit ventilation the baseline building design whole-unit ventilation rates in all dwelling units shall be modeled using the same rates as the Proposed Design, without exceeding ASHRAE 62.2-2007 recommended rates by more than 50%. If the whole-unit ventilation in the Proposed Design exceeds ASHRAE 62.2-2007 rates by less than 50%, the Baseline shall be modeled the same as the Proposed Design. However, if the ventilation in the Proposed Design exceeds ASHRAE 62.2-2007 by more than 50%, the Baseline shall be modeled at rates that are no more than 50% greater than the rates recommended by ASHRAE 62.2-2007.”

“3.12.3.5 Mechanical Ventilation Rates. The mechanical ventilation rates may differ between Baseline Building Design and Proposed Design if the Proposed Design has specified rates more than 50% greater than ASHRAE 62 recommendations, resulting in the energy penalty associated with over-ventilating.”

Do these statements apply to my project? Can I model the baseline with OA supply 50% higher than the specified in ASHRAE 62.1 2010?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/13/2019 - 15:18

1. Yes those statements apply. 2. Maybe. It depends on how the two ventilation standards compare. You will need to compare your design using 62.2-2007 to see if it is +/- 50% of that standard. You can't use 62.2 and 62.1 interchangeably. 

Thu, 02/14/2019 - 19:45

Thank you Marcus.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.