Data-Centers-NC-v4 EAc2:Optimize energy performance

Number of chillers in Energy Model

Hi, I am currently preparing an energy model for a data center project (system 8). Since the process load is very high, 22 chillers and cooling towers are required if I stick to the requirement in Appendix G Table G3.1.3.7 which states that no chillers shall be sized larger than 2813kW. Have I missed something, perhaps an exemption somewhere, because this seems a bit odd.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/10/2015 - 15:03

It depends. Cooling a data center could be considered a process load. If the cooling system cools the equipment directly it might be considered a process load itself. Then it would be modeled identical to the proposed.