FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

no cooling / using addendums

Hello, I have two questions: 1) we are working on residential building where its occupied spaces has heating and cooling, but rooms situated on north facade has no cooling system. Whole building floor area is 5 600 m2 (60 277 ft2) and these rooms without cooling are only 340 m2 (3 660 ft2). My question is how I should model the proposed HVAC system regarding to Table G3.1.10d where is stated: "where no cooling system exist or ......., the cooling system shall be identical to the system modeled in the baseline building design." I think this is definitely not my case, I think this can be applied where whole building has no cooling system. But can I leave these rooms without any cooling and in baseline building the cooling system will be present? 2) It is not clear to me if I have to use addendums to ASHRAE Standards or not. Or just some addendums? I am sorry for maybe dumb questions but I rather ask than stay in confusion. Thank you in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/21/2015 - 13:28

Technically you are required to model cooling the both cases in the whole building. You are however allowed to model a high temperature set point in the spaces without cooling so that they system never operates. What we do is tell the reviewer that we could model a cooling system where it does not exist and set the temperatures high enough for it not to operate but have not done so because it is a waste of time. We then just model the proposed as designed and model the corresponding areas in the baseline without any cooling, just as in the proposed.

Tue, 07/21/2015 - 14:00

Thank you very much Marcus for quick reply. I like your way how to deal with it. And what about my second question, because now I dont know if using Addendums is required or I should forget about all Add. and just work with "first edition" of Standard 90.1-2007 and issued Erratas. Because Addendum r completely changes Appendix G or Addendum g changes some U factors etc. So I dont know... Thanks

Tue, 07/21/2015 - 14:30

You are not required to use any of the addenda. You should only use an addenda if you need to do so. Some of them are very helpful depending upon the issues in your models. Keep in mind that if you use an addendum you must use it in its entirety.

Tue, 07/21/2015 - 14:47

OK, now I understand. Thank you Marcus!