I have a very small elevator lobby, which has a little mini-split unit without outside air. It is the main entrance for an apartment building, and every time it is occupied, there will be an open door letting in large quantities of outside air. Tenants can literally only go from the elevator lobby to their own apartment due to lockouts in the elevator controls. Once they are there, the elevator returns to the first floor waiting for the next occupant. By the VRP compliance calculator in the IEQp1 Appendix, it would require 6 CFM of outside air to comply with IEQp1 and IEQ C2. I'm arguing for allowing this on two grounds:

1. IEQc2 Case 2 Option 2 Naturally Ventilated Spaces requires compliance for "at least 90% of occupied spaces". This space is about 0.4% of the building's floor area. All other spaces comply with mechanical ventilation +30%. Thus the requirement for "at least 90% of occupied spaces" is met.

2. Although the opening is not a window, the opening will be opened absolutely every single time the space is occupied, since people enter the space to get on the elevator or exit the elevator and leave the building. There are no chairs, waiting areas, or other reasons a person would be in the space for any time. (there will be, hopefully, a handsome LEED plaque which they may admire) A resident will almost always enter the front door, and walk right into the open elevator. A resident leaving the elevator will walk out the elevator door and leave the space. Such occupancy will always be brief, on average a few seconds. Thus the space will always be well ventilated whenever the space is occupied.

Do you think they'll buy this?