NC-2009 IEQp1:Minimum indoor air quality performance

Natural ventilation

We are working on a residential core and shell project, and we are having some issues with the compliance of ASHRAE 62-1 ventilation requirements. Basically, the building has apartments on each long side and a central corridor that goes all the way through. All of the rooms include a operable window of 4% of the area within 25 feet, except a small service room that would only have a window to the corridor; therefore it would be ventilated through the adjoining space. Now, this central corridor is completely open to the outdoors on its sides; could we use the 4% rule, or do we need to go with 8% or 25ft2 minimum? The problem is that a 25ft2 window on that tiny space would be unreasonable. Thank you for your comments.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/02/2014 - 20:24

Is the 'service space' an occupiable space that requires ventilation under ASHRAE 62.1? If it is a mechanical closet or non-occupiable storage closet, you may not be obligated to provide ventilation.

Thu, 10/02/2014 - 20:30

Yes, it is actually an occupiable space that requires ventilation, Thanks!