5.2 is satisfied by submetering each tenant space independently. For 5.1, you really need to start with your M&V plan. First decide which IPMVP path you are following. The answer to questions 1&2 above depend on the M&V plan you develop. If the fans are AHU fans, one per tenant, then typically they would be metered individually. I would probably not meter each pump, but would instead trend data from the pump VFDs through the BAS. For question 3, it is certainly appropriate to calculate some end uses, rather than metering them directly. If you've metered the total, and everything but "x", you know "x" as well.

Wed, 08/25/2010 - 12:01

Actually, you could also gather data for each AHU in the manner I described for the pumps. But for utility consumption accountability, you probably want AHUs serving a single tenant on the tenant electric meter.

Wed, 08/25/2010 - 13:30

Thanks Christopher! I am using Option B: Energy Conservation Measure Isolation. I understand from you that every AHU Fan is to be metered alone. Regarding the pumps, if I want to install submeters (and not trend data through the BAS), should I install for each of the primary and secondary pumps? Many thanks!

Wed, 08/25/2010 - 13:36

If this is new construction and/or the ECMS implemented are interactive, Option B may not be appropriate. Under Option B, you need to meter the ECMs you have implemented. To your specific question, I'm struggling to understand what you'd learn by metering the pumps individually. Again, first develop the M&V plan. Design the metering per the plan.