Must C&S HVAC certified under 62.1-2004 upgrade to 2007 for CI?

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 03/28/2010 - 13:54

David, The TI spaces need to meet 62.1-2007. A plus: the ventilation rates are the same for most space types between the 2004 and 2007 versions. You do have to be careful to show compliance with 2007 on a space by space basis within the TI area. Some designers run into problems when TI spaces have a high proportion of densely occupied areas (like conference rooms) and the CS HVAC system only accounted for an open plan office, for example.