Forum discussion

CI-2009 IEQp1:Minimum indoor air quality performance

Multi-zone system when single AHU supplying OA to FCUs?

We have 2 AHUs supplying OA to individual FCUs via a separate duct as per ASHRAE 62 intake requirement. The mixing occurs at the individual FCUs and then supplied to the zone. In such a scenario, should we consider it a Multiple-zone system or single-zone system? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/14/2013 - 13:49

Poorva, if an individual FCU provides ducted supply to more than one zone (with significantly different thermal load characteristics), you'll still need to use the multi-zone calculation approach in ASHRAE 62 for each FCU. If the FCUs are zoned appropriately, you'll be able to use a single-zone approach, which simplifies the required calculations.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.