Forum discussion

NC-2009 EAc1:Optimize energy performance

Modeling Snow-Melt Systems

I am modeling a LEED building that includes a snow melt system. The system is served by the building's hot water boiler. This boiler also provides hot water to the coils within the building's air handlers. My first dilema is: Should I clasify the snow melt hot water load as a Process Load on the LEED Online template? My guess is no since I can estimate the annual snow events from weather history which will allow me to calculate the time in which the system will run. Additionally my boiler is 95% efficient, which exceeds the efficiency of the baseline boiler. (Process loads must be identical in the proposed and baseline model, unless a narrative is provided) My second dilema is: ASHRAE 90.1 Appendix G requires me to provide heating and cooling to all conditioned spaces, do I model an in-slab cooling loop in addition to my in-slab radiant loop? My guess is no since the slab is technically not within a conditioned space. This is the first time I have modeled a snow melt system since our state code did not allow this system until recently. (unless the snow melt loop is served by the building's waste heat. . . Miller Brewing company has this type of system) Thanks in advance for any comments or insight anyone can offer. -Dave Hubka

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/11/2011 - 14:17

Yes it is a process load and will need to be indicated as such on the template. You will need to do an exceptional calculation since you will be claiming savings for this process load. The cooling system you must put in the proposed model, if the building does not have one installed, should be idential to the one in the baseline system.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.