I have had this doubt from a long time, is the occupancy assumed for IEQ calculations related to FTE?, and if so, in which wa?,
Thank you
Forum discussion
NC-2009 IEQp1: Minimum IAQ Performance
I have had this doubt from a long time, is the occupancy assumed for IEQ calculations related to FTE?, and if so, in which wa?,
Thank you
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Is outdoor air quality testing required in a space using natural ventilation?
What options are available to projects outside the US to meet this prerequisite?
Can LEED 2009 projects elect to follow ASHRAE 62.1-2010 for this prerequisite?
Which units should be included in the calculations for this prerequisite?
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
542 thumbs up
March 12, 2013 - 10:31 am
FTE is required when performing this prerequisite for existing buildings, not new construction.
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
March 12, 2013 - 12:48 pm
I have seen USGBC review comments saying that the occupant load with diversity should be within 10% of the FTE for ASHRAE 62MZ calculations. That, to me makes logical sense fr most buildings. If the two are not within 10% for some reason (i.e. I did not calculate spaces that were not considered to be potentially critical) then I always include that as a comment in the template.
Hernando Miranda
OwnerSoltierra LLC
344 thumbs up
March 12, 2013 - 1:09 pm
The USGBC's LEED Department linking of FTE to ASHRAE 62.1, and the automatic assumption that heating is the dominate ventilation mode for conference rooms, does not take into account that heating occurs during low diversity, and cooling occurs during high occupancy.
ASHRAE 62.1 should consider occupancy based on expected occupancy. I have that case for a building with a current FTE of 1 per 1,000 sf. The FTE might increase in the future, but that depends on the business climate. The building has seven ventilation systems. We are using the default ASHRAE 62.1 occupancy densities rather than actual FTEs. This makes more sense than using actual FTEs.
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
March 12, 2013 - 1:13 pm
Hernando, it sounds like you are using a reasonable approach to your design. I would just go ahead and explain why it differs from the FTE. I have never seen them comment on it unless your 62.1 calcs show a lower occupant load than the FTE's.
Hernando Miranda
OwnerSoltierra LLC
344 thumbs up
March 12, 2013 - 1:25 pm
Tristan, even though the FTE is not referred to in the Reference Guide it does appear as a review comment if the total occupancy used in for ASHRAE 62.1 is not consistent with the PI Form FTEs. I think this only occurs when the FTE is lower for ASHRAE 62.1, and not when it is higher.
Hernando Miranda
OwnerSoltierra LLC
344 thumbs up
March 12, 2013 - 1:31 pm
Andrew, I am relatively certain this only occurs with low ASHRAE 62.1 FTEs. What triggers the review response, like other LEED responses, is that it is not explained in the LEED Reference Guide. I can't find a published reference to the 10% difference in occupancy counts. Yet, it is required.
Paula Hernandez
MRS.PAH&A
85 thumbs up
March 12, 2013 - 2:00 pm
Tristán, David, Andrew and Hernando,
Thank you all for the responses, as far as I can understand before this discussion, number of people used to comply with Std 62.1 is supposed to be 10% within FTE, but I have a 100% OA system, so the calculations are easier, I have no diversity.
And of course this occcupancy has to be the same used for the energy modeling ....is that so???
Weidong Luo
Ecotech InternationalApril 2, 2013 - 1:05 pm
this occcupancy has to be the same used for the energy modeling?
Can anybody confirm the above?Thanks,
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
April 2, 2013 - 1:29 pm
The ASHRAE 62.1 occupancy (including diversity) should be within 10% of the project FTE. You should use the EAp2 forum to ask the question of whether or not the energy model needs to be within any percentage of the FTE occupancy.
Weidong Luo
Ecotech InternationalFebruary 4, 2014 - 6:21 am
when you talk about within 10% of FTE, you actually mean total building users at peak moment (see PI F3) by FTE, right?
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
February 4, 2014 - 8:19 am
No, I mean FTE as in the full time equivalent occupants. The peak total could be much higher than what you need to use for ventilation design. If you familiarize yourself with ASHRAE 62.1-2007 then you will find that you design ventilation for the number of occupants normally in a space. In a large space of intermittent occupancy you may use a time average based on the equations in the standard. Your ventilation occupancy load will (for most buildings) reflect the FTE number +/- 10%. If you are higher due to an unusually high number of transients then just explain that in the template. You should never submit if you are more than 10% lower though.
Weidong Luo
Ecotech InternationalFebruary 4, 2014 - 9:27 am
Thanks, Andrew. For a project with 35 FTEs and over 300 transiets at peak moment, Although the ventilation occupancy adjusted by diversity factor and/or time average would still be far beyond FTEs, submitting with explanation may work, do i get it right?
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
February 4, 2014 - 9:56 am
Yes, just explain this on the form.
Julia Weatherby
PresidentWeatherby Design & Co. Engineers
94 thumbs up
February 4, 2014 - 9:59 am
Weidong Luo, yes, as Andrew says just explain in a narrative how your design occupancy for IEQp1 is related to the number of FTEs and transients. As long as you have a reasonable explanation that is consistent with what you have stated in other credits, it should be accepted.
As a general comment on this topic, I see this statement in the LEED project submittal tips for NC2009 IEQp1: "Be sure that the total peak occupancy and square footage documented for this credit is reported consistently across all credits."
The LEED Project Submittal Tips for several 2009 rating systems can be downloaded at:
http://www.gbci.org/main-nav/building-certification/resources.aspx