Method to Achieve Thermal - Comfort for Ventilated Area

Hai Everyone:- Our project is sewing factory It is not fully conditioned (A/C & Ventilation) 1.A/c for Office area 2.Fans (Exhaust, Fresh air, HVLS fans) for Production area We use HVLS fans for lieu of A/c Is it possible to attend this credit using HVLS fans in Ventilated Areas HVLS fans are Circulating fans are not

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/11/2015 - 21:46

It sounds like you might have a hard time complying. What are the temperature and humidity conditions in the production area?

Tue, 01/05/2016 - 07:51

Temperature is about 31 deg C and above and MET rate is 2+ Is it possible to get this credit using Design alternative (MET - above 2)

Mon, 01/25/2016 - 15:44

31 C = 88 deg F. That's warm. With a MET rate of 2 I don't see how you can possibly comply. What you have is a literal sweat shop.