Hi, For one of the LEED CI project, the developer has provided louvers with motorized dampers in the AHU for fresh air intake. Can the louvers qualify for fresh air intake? if Yes, then how do we account this in the VRP calcualtion. Or is it necessary the fresh air inline fans to be provided in the AHUs.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Add new comment
To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.