Does anyone know if for ventilation requirements Title 24 - 2005 is acceptable in lieu of ASHRAE 62.1-2007? I know for EAc1 Title 24 - 2005 is seen as equivalent to ASHRAE 90.1- 2007. Additionally, it is written in the book that "local code can be used in lieu of ASHRAE when the local code is more stringent."
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
November 23, 2011 - 10:40 am
This one is challenging to answer, because T24-2005 doesn't include the same procedures as ASHRAE 62.1 for multi-zone recirculating systems (e.g. VAV). If you're working with a dedicated outdoor air system and the effective airflow rates are greater per person than ASHRAE 62.1, then I think it's fine to use T24.