CS-2009 EAc5.1:Measurement and verification - base building

List energy end uses

"The M and V Plan omits the table or listing of the project’s energy end uses as required by the form." However, the Plan we have submitted lists the following: Locations and types of energy meters are shown on drawing 10610/35008. The following energy types are metered: Electricity LTHW Chilled water Domestic water Softened Water Gas Is there any additional details that need to be listed regarding the energy end uses?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/18/2013 - 13:55

Energy end uses are not the same as energy sources. Energy end uses are typically interior lighting, exterior lighting, space heating, space cooling, fans, pumps, service hot water, plug loads, elevators, etc. You cannot properly calibrate an energy model using just metered energy sources.