I'm working on a project and the owner selected a decorative post top fixture to line the drive into the site. The site is small enough where this fixture is the main site fixture. One look at it and I said it won't comply with SSc8. I was told to look at it and do what I can. The fixture had 10% uplight. Then I was told it had a special glass optic to limit uplight. That knocked it down to 4% uplight. This is in an LZ2 location so I need a total site uplight of 2% or less. I thought I'd try for Pilot Credit 7. I imported the IES file into Visual's photometric viewer to see it's BUG rating. It had a U3 rating. Tried the lowest wattage version of the fixture and it's still U3 rating. I looked closer at the values and realized they already updated the software to TM-15-11. But PC7 is based on TM-15-07. The uplight values were reduced from 100 lumen in '07 down to 50 lumens in the '11 version. This low wattage version has 88 lumens in one of the uplight zones. So it is actually a U2 rating until LEED v2012 comes out. Just found it odd that this fixture can be non compliant for SSc8 in both v2009 and v2012 but manages to comply with PC7.