CS-v4 EAp2:Minimum energy performance

Lighting Power Modeling for Core and Shell Building

Hi,

I am trying to model the lighting power for a core and shell office building, the lighting is designed for the core spaces such as main lobby, restrooms and BOH, but the tenant spaces are not. I am thinking of the below approaches to model the lighting power in the energy model:

Building Area Method: in the proposed building calculate the total designed lighting power and use 0.9 W/sf (from Table 9.5.1) for the tenant spaces, then added them together and divided by the total building area which resulted in 0.88 W/sf. For baseline building I used 0.9 W/sf

Space-By-Space method: in the proposed building I used the actual power for designed spaces and 0.9 W/sf for tenant spaces to meet the requirement of Table G3.1.6 (proposed)(c), "where lighting neither exists nor is specified, lighting power shall be determined in accordance with the Building Area Method for the appropriate building type”. For baseline building I used Table 9.6.1 to get the power for designed spaces and 0.9 W/sf for tenant spaces.

Are these approaches seem reasonable for each method?

 

Thank you,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/10/2019 - 15:35

You have to use the building area method and the LPD must be modeled identically in both models. If you want to claim any savings you must include requirements in the tenant lease agreement.

Wed, 04/10/2019 - 15:53

Thank you Marcus, for the tenant spaces we are not planning to claim any savings, but the lighting power is designed for the core spaces. Would my approach above for the BAM be appropriate to address these designed lighting power?

Wed, 04/10/2019 - 16:36

No. The values you used must be kept separate. The reviewer will not be able to determine that you modeled the tenant spaces identically otherwise.

Wed, 04/10/2019 - 16:54

Understood, What if I calculated a W/sf for the designed spaces and modeled the tenant spaces identically at 0.9 W/sf? will that be a better approach?

Wed, 04/10/2019 - 16:59

The designed space in the proposed model must be modeled as designed. This is what needs to be separate. The baseline could all be the BAM value for an office.

Wed, 04/10/2019 - 17:14

Thank you!