Hello-
I wanted to get some clarity on LEED Interpretation 10498- https://www.usgbc.org/leedaddenda/10498
My project is a core and shell building in California with offices as the future tenants.
The baseline building follows the ASHRAE 90.1 LPD for office spaces as 0.90w/sf. The finished spaces (core zones- restroom, storage, electric, mechanical rm) in the proposed building use as-designed LPDs and the unfinished spaces (future office) uses 0.72w/sf based on the Table 1 in the LEED interpretation.
Is this methodology accurate??
LEED reviewer mentioned that there needs to be ONLY two LPD numbers- finished and unfinished spaces using the weighted average method.
Finished spaces should use the weighted average method and not use "Individual" LPDs. The reason being- ASHRAE doesnt allow that "Building type methodology" and "space by space methodolgy" should not be combined.
Have any of you come across this?
I just want to understand the "right" way to model LPDs in the future.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5868 thumbs up
December 5, 2022 - 4:19 pm
Based on the Interpretation your comparison sounds right to me.
Not allowing the mixing of Building Area and Space-by-Space methods has been a very long standing rule for LEED projects.