Hi All, I do need help in the energy modelling for a warehouse project. Thanks in advance! This project consists of 200,000sf of warehouse with 5,000sf office space. The warehouse is heating only; the office uses heat pump for both heating and cooling. Now the questions came: 1. Do I need to model a cooling system in the proposed model? 2. Which baseline system shall I use? From Appendix G, system 7 should be selected. But I doubt if it is applicable for heating only space. 3. Shall I apply two baseline HVAC systems? or just use one dominant system? Many thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/11/2016 - 13:46

1. Model a system 9 or 10 from 90.1-2010 by using the addendum that created it. 2. You subtract the area of the warehouse from the total and use the remainder in Table 3.1A. Looks like a system 3. 3. Yes two baseline systems.