Hi,
I have an high rise residential project and the property wants to permit people to smoke on the balconies.
My question is: the Tests for leakage are to be performed on each dwelling units or is it possible to reduce the tests to some rapresentative unit? (for example, typological apartment or typological square meter).
Thank you very much for your help.
Regards
Trista Brown
Project DirectorWSP USA
449 thumbs up
November 12, 2019 - 3:52 pm
Hi Mario, the v4 Reference Guide says "A sampling rate of at least one in seven smoking units can be used, per the Residential Manual for Compliance with California’s 2001 Energy Efficiency Standards, Chapter 4." I don't believe this has changed under v4.1.