ASHRAE 90.1-2007 Appendix G states for baseline system types: "For laboratory spaces with a minimum of 5000 cfm of exhaust, use system type 5 or 7 that reduce the exhaust and makeup air volume to 50% of design values during unoccupied periods."
Should this statement be interpreted as if the sum of all lab exhaust on a particular system is greater than 5000 cfm or if an individual lab space is greater than 5000 cfm?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
November 12, 2010 - 8:45 am
Our interpretation is that the 5000 cfm applies to the exhaust system not each space.
Any other opinions?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
June 4, 2015 - 10:41 am
1. I don't know EnergyPro well enough to say.
2. Proposed is modeled as designed.