Infiltration rate @ 75 Pa (ASHRAE 2016) vs. 4 Pa / 50 Pa (Design Builder Software)

Hello, 

ASHRAE 2016 specifies the infiltration rate of the building at 75 Pascals (2.03 L/s.m²).

However, as I am modelling my building on Design Builder version 7, the options for the infiltration rate are at 4 Pa, 50 Pa, or simply Vol/h.

Can someone tell me how to enter into my model the equivalent of the value specified in ASHRAE 2016?

Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/01/2023 - 14:44

You can convert the rate for different pressures. Here is a tool to do so - https://www.evokebuildings.com/airtightnesscalculator Here is an article with a simple formula - https://help.covetool.com/en/articles/2626652-infiltration