infiltration

If I model a building where there is mechanical ventilation, how shall I consider the infiltration (i.e. "uncontrolled inward air leakage to conditioned spaces through unintentional openings in ceilings, floors, and walls from unconditioned spaces or the outdoors", see ASHRAE 62.1-2007)? Suppose that no blower door test was made. Generally I model a constant value of ACH, which I determine according to my experience, but shall I respect any particular document (e.g. an ASHRAE standard)? With Regards

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/10/2013 - 15:47

Infiltration can be modeled however you like but must be identical in both models. Unfortunately as far as I know no baseline has been established by ASHRAE so projects cannot claim savings for infiltration reductions. Is anyone aware of an attempt to establish infiltration baselines, perhaps as part of the development of 90.1-2013?

Thu, 01/10/2013 - 16:09

Very interesting subject. The non-Residential Alternative Calculation Method (ACM) from the Califormia Energy Commission states that the infiltration rate should be 0.038 cfm per square foot of gross exterior partition (walls and windows) area for the zone. For new buildings, I agree with you Marcus that no savings can be claimed. However what about heavy renovation of existing buildings?