CI-v4 WEp1:Indoor water use reduction

Indoor Water Usage Prerequisite Requirements

In the reference guide of LEED ID+C V4,  it is mentioned under prerequisite  the newly installed plumbing fixtures must be according to the Table 6 flow rates. The % savings must be shown for each fixture from LEED baseline and all fixtures must be water sense labelled.

However , there are 2 compliances path mentioned under the same requirement, Compliance path 1 Prescriptive: is for % savings achieved for each fixture , Compliance path 2: usage based calculation i.e. showing cummulative savings of atleast 20% based on usage , occupancy etc.

Currently in India water sense labelling is not followed.

I have attempted by compliance path 2 by showing % savings on usage basis, for prerequisite and for credit.

I want to know is it still mandatory for fixtures to follow the flow rates in Table 6 , or usage based calculation and manufacturer cut sheet with flow rate data sufficient???

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/15/2022 - 21:29

Hi Rakesh, Sorry for the delayed response; I guess this post slipped past me/us. I still want to respond in case it's still needed, or if others have the same question. Let me recap so I understand the ask:
  • Project is in India; India does not have an equivalent program to Watersense, therefore, the project must meet at least a 20% reduction in fixture rates shown as baseline in the Ref Guide.
    • Since you are using Path 2, no, Table 6 does not apply as it is there as guidance for Path 1.
  • For Path 2, you would submit the water use reduction calculator, with fixture cut sheets showing rates. You may also want to reiterate to the reviewer that the Watersense requirement does not apply.
Hope that helps.