NC-v4.1 EQc1:Enhanced Indoor Air Quality Strategies

Increased Ventilation - Strategies 5 and 6

Hi all,

Curious if anyone has pursued the newest v4.1 language going after six out of ten possible strategies for 2 pts and have looked at Strategies 5 and 6 for increased ventilation. Would strategies 5 (Increased Ventilation 15 Percent) and 6 (Increased Ventilation 30 Percent) both count towards your total strategy count? For example, if a project goes for the 30% outdoor air increase the team would also inherently achieve the 15% increase (strategy 5). Any thoughts/experience with this?

Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/06/2021 - 19:05

yes, a project that achieve 30%+ would also achieve the 15% threshold.  (2) strategies complete, (4) more to go! good luck.

Wed, 05/18/2022 - 17:48

I can confirm that a project of mine was recently awarded both strategies by achieving 30%! Woohoo!
 