FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

If some facades meet ASHRAE 90.1, but others don't....

....does the project meet ASHRAE 90.1's Mandatory Provisions and therefore this Prerequisite? Our project has complicated set of facades with different curtain-wall patterns and types of glass. Two of those facade directions comply with the ASHRAE "Mandatory Provisions" requirements for SHGC, while the other two do not: the requirement is a SHGC for each facade of 0.25 and two facades are 0.203 and 0.245...the others are 0.266 and 0.264. Will this project be rejected for this prerequisite based on these figures?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/13/2013 - 00:35

SHGC is not a mandatory provision. It is available for trade-off.

Mon, 05/13/2013 - 05:34

That's good to hear. So a "trade-off" basically means that we can have a deficit in one area/facade as long as it is made up in another area: as long as we balance out with an overall performance that meets the standard we are ok? For example: if the requirement is 0.25 for all facades and we have 0.20 for two facades and 0.30 for the other two, then we are compliant.....did I understand that correctly? Thanks in advance.

Mon, 05/13/2013 - 12:33

Trade-off means you can exceed a prescriptive requirement of 90.1, like SHGC, by as much as you want. You do not need to balance some under SHGC with some over. Trade-off is general and not specific. Basically you are trading-off being over the SHGC for some glass with exceeding the prescriptive requirements in other areas, could be some other glass SHGC or higher insulation or greater cooling efficiency, etc.. The trade-off is against other energy saving measures. The only requirement is that you be able to show the minimum energy savings required by the LEED prerequisite.

Mon, 05/13/2013 - 13:13

Thank you Marcus! This makes so much more sense now. Why is ASHRAE's writing so cryptic? To be answered another day.