Regarding IEQp1 and VRP Compliance Calculator there is a question on how to enter an AHU having the following characteristics:
The AHU is a constant volume device; supplying to several rooms, but with one and the same temperature; It is 100% OA unit.
The question is:
Should such AHU be entered as "Single Zone Unit" or as "100% Outside Air".
Thanks.
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
January 5, 2016 - 12:33 pm
Vassil, this should be modeled as a 100% outside air system, which will simplify some of the calculations.
Vassil Vassilev
ManagerTermoservice
13 thumbs up
January 6, 2016 - 1:12 am
Thanks for the reply.
Regarding the simplicity of calculation, the Single Zone is even more simpler than 100% OA. Besides, the AHUs for these zones are the only HVAC equipment to cover the thermal loads there and that was the reason for the question.