Forum discussion

EBOM-2009 IEQp1:Minimum indoor air quality performance

IEQp1 compliance for high-rise with 1 outdoor air intake

The 1987 high-rise building in California I am attempting LEED certification for has an EnergyStar label and, thus, was signed off by a PE as meeting ASHRAE 62.1/2007. The building has only one outdoor air intake that is 100% open at all times and cannot be modified. The PE established the building met ASHRAE 62.1 by measuring the Outdoor Air (OA) CFM coming into the building at that intake unit. He also measured the outside air CFM into the Air Handlers at three floors of the building - the top floor, a middle floor, and the bottom floor. If these measurements were sufficient for the Energy Star label, are they also sufficient for LEED, or do I need to take measurements at the Air Handlers on every floor? Thank you for any information you can provide.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/09/2011 - 14:01

The prerequisite requires applicants to demonstrate that each outside air intake, supply air fan, and/or ventilation distribution system supplies the minimum outdoor air ventilation for each air handling unit. I would expect the LEED reviewer would ask you for OA measurements at every AHU. The LEED online template requires the reading to be taken during the performance period. Hope this helps.

Fri, 12/02/2011 - 12:59

Does this mean that for compliance with IEQp1 we will need to demonstrate calculations (from ASHRAE 62.1) that show the required OA rate, AND take measurements at each AHU utilizing the OA proving that we meet the calculated rate? Or would it be sufficient enough to take measurements at only the units supplying OA (i.e. if you have a large MAU that distributes ventilation air to multiple FCU's, do you need to measure OA at each FCU or simply measure the OA supply at the main MAU?)

Fri, 12/02/2011 - 15:08

LEED requires OA measurements to be taken at the system level. If you have a large make-up air unit that distributes OA to numerous fan coil units you will need to take OA measurements at each fan coil unit. i.e. the fan coil units are considered to be "the system level".

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.