We have a VAV system where single AHUs serve multiple zones. Do we need to take outside air measurements at each VAV box?

Our building has a single fan that supplies outside air to multiple AHUs. Do we need to perform outside air testing at the supply fan or at all AHUs?

What if our systems do not meet the required outside air when systems are tested at worst-case conditions?

What if after our Preliminary Review we have to revise the ventilation rate procedure calculations and find that we need to make corrections to the system in order to meet the prerequisite? Can we redo the outside air testing after making corrections? Wou

My building has 80 AHUs providing ventilation to building spaces. Do I have to do the ventilation calculations and conduct outdoor air measurements for each one?

Our system cannot provide enough outdoor air to meet ASHRAE 62.1-2010 due to design limitations. How much outdoor air must we provide to meet Case 2 instead?

The outdoor air intake for our ventilation system is not accessible, and it’s not possible to measure the outdoor airflow directly. How can we determine the outdoor airflow for this system?

How do I find whether my project is located in a non-attainment area for particulate matter or exceeds the prerequisite ozone requirements?

What happened to the IEQ Space Matrix that was available to version 2009 projects? What should I reference to determine how spaces in my building should be categorized for this prerequisite?

View answers »

Forum discussion

EBOM-v4 EQp1:Minimum indoor air quality performance

IEQp1 - calculator

My greetings I am working through In the IEQp1 Minimum Indoor air quality performance and I need orientation with respect to systems with natural ventilation. I need to know if exists a calculator that allows me to enter the data of airflows, in case it was not, what would be the steps to follow to make the documentation of this pre-requisite. Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/31/2017 - 23:40

There isn't a calculator that I know of to assess compliance with the natural ventilation criteria in Section 6.4 of the ASHRAE standard. This prerequisite presents another important challenge for naturally ventilated buildings. ASHRAE 62.1-2010 effectively prohibits natural ventilation as a standalone strategy unless the openings to the outdoors that provide ventilation are permanently open or are controlled open during operating hours. There are a couple of other exceptions to this. Check out the exceptions in the ASHRAE standard or the online LEED reference guide.

Wed, 02/21/2018 - 12:08

Hi, Ben I'm working on a project with natural ventilation only, but it has air conditioning systems (mainly simple split system). Looking at the prerequisite template text: "Provide documentation demonstrating the minimum outdoor air opening and space configurations meet or exceed the minimum values from the natural ventilation procedure outlined in ASHRAE 62.1-2010, Section 6.4." I concluded that the effective requirements are the windows' opening sizes and the spaces' layouts, in order to comply with the maximum distances from the same openings. Because, otherwise, many projects will be unfeasible to comply with this prerequisite.

Thu, 06/14/2018 - 23:10

Hi Patrick,  That's true that the natural ventilation procedure assesses the window sizes and space layouts. However, the section 6.4 begins by stating that "natural ventilation systems shall be designed in accordance with this section and shall include mechanical ventilation systems designed in accordance with Section 6.2 and/or Section 6.3." it then goes on to state the exceptions to the requirement to provide mechanical ventilation systems as follows.  The mechanical ventilation systems are not required
when: 1. Natural ventilation openings that comply with the requirements of Section 6.4 are permanently
open or have controls that prevent the openings from being closed during periods of expected
occupancy, or 2. The zone is not served by heating or cooling equipment.