Hello All,

I am working on a school project. The ventilation is "Mechanical Ventilation 100% Outside Air" +natural ventilation in all of the classrooms. There are several multiple zone AHUs and several single zone AHUs.

I use v.4 of the online form.

I chechked the box "Mechanical Ventilation 100% Outside Air" and started filling in table IEQp1-A3.

Do I need to fill anything exept these tables?

I have noticed the following while filling in the IEQp1-A3 table:

There is NO fieled where one can fill in the Project Design Outdoor Airflow for EACH SEPARATE ZONE so that the table can compare the results zone by zone. At the bottom of the table there is the SUM of the Vot values for all zones and under it one is asked to fill in the Project Design Outdoor Airflow for the AHU.

In this case one can be below the Voz for several zones but still will manage to comply to the credit if he has more flow than the required in other zones of the same AHU.

Am I correct or do I miss something because this seems terribly wrong?
(I have asked this question in other section of the forum by mistake, sorry)