IEQ Credit 5 - Supply Air Recirculation

In our project, we have a janitor room adjacent to a toilet and these both rooms have exhaust duct which are combined together & exhausted directly to outside without re circulation. But, we have common a fan coil unit to these rooms (i.e, supply air is going to both rooms & return air is taking from both room). Also,fresh air is provided to these room via FCU (in false ceiling) and both rooms are negatively pressurized. Our concern is that return air from janitor room is going to FCU & this same FCU is serving toilet also. Will this affect our IEQc5 credit ?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/30/2016 - 22:48

Recirculation is not allowed for this credit.

Sat, 04/09/2016 - 21:01

Why not just duct the return for the fan coil unit into the hallway. Then you wouldn't have the recirculation issue.