I am currently working on a LEED v3.0 model in trace 700. It is a historic building originally built in the late 1800s. It has a variety of unique situations that I am unsure of how to model. The project is being renovated in multiple phases. We have received permission to model only the wing that is currently being renovated for our LEED application. An earlier phase of the project installed a chiller to serve the entire building. The chiller is not located within the wing we are modeling and the cooling towers are located across the street where the district heating plant is located. I am using Option 1 (building stand-alone scenario) for the district heating. I would like to model the chiller so I can gain some credit on the plant level. Is this allowed given this situation? If so, how should I model the chiller since it serves the whole building and only a quarter of the building is being modeled?

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/20/2011 - 14:43

In similar situations we have been allowed to proportion the load on the chiller associated with the new wing and model that. I think that was a v2 project however. There is a 90.1 provision that says you must model the whole building. So check the interpretations to see if the one we wrote for the project I mentioned above is still in place. If not then you should probably submit a new interpretation request.