How to fulfill requirement for Envelope Compliance?

We are doing a LEED ID+C project, going for V4.1. We got a comment from GBCI under EAp2 that we need to provide envelope compliance form. But, as a interior project we have no control on the building envelope and the building is pretty old, and not fulfill the ASHRAE latest standard. How to resolve this issue then?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/22/2024 - 14:26

Which option are you pursuing? Are there any envelop improvements (i.e. work done on exterior walls or window replacement) included in your IDC scope of work?

Fri, 09/20/2024 - 07:54

If no envelope modifications are included in our scope of work for the LEED ID+C project, how should we set up the Baseline and Proposed models for energy simulation? Does this mean we are exempt from complying with the envelope Mandatory Provisions under ASHRAE 90.1-2016?

Fri, 09/20/2024 - 12:32

The proposed should be as it currently exists. The baseline should be according to 90.1-2016 minimum. You do not have to meet the mandatory provisions for envelop because you are not upgrading the envelop therefore the code requirements do not apply.

Tue, 09/24/2024 - 02:27

In such case envelope wasn't modeled – interrior was completely interrior %^), in my case it was: "As it is an interior space with no contact with outdoor environment, we model only adiabatic partition walls" in proposed and baseline cases.
Envelope compliance wasn't seeked.