NC-2009 IEQp1:Minimum indoor air quality performance

How to calculate effective operable area for top hung window

Hi, We are in the initial design of an office building. The Project team has planned to provide top hung window & the building will have more naturally ventilated spaces. How to calculate the effective opening area / operable area to check 62.1 compliance & also the opening angle will vary based on its direction. Is there any procedure or table to calculate the opening area considering the angle. Also please let me know the same for side hung windows. Thanks..

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/17/2014 - 13:09

For an awning type window like you describe I have seen projects use 100% of the area that is movable and this was accepted by USGBC. I would not use this as the case if the window does not open at least 45 degrees. If it is less than that then you should do a geometrical representation to show what area you are using. That is how I would approach it. For side hung (swinging) windows I believe they can open 90 degrees and thus 100% is definitely applicable.

Sat, 01/18/2014 - 05:31

How to do geometrical representation to show openable/operable area?. Because in our project, the angle is 30 degree. Please help to proceed further? Is there any standard to follow at this kind of situation?

Mon, 01/20/2014 - 14:46

I would draw the window open in both plan and elevation view and show the actual area open to the outside. This would be a rectangle for the bottom horizontal plan and a triangle on each side for the vertical plane.

Tue, 07/22/2014 - 19:35

Andrew, I may have the same case they posted here, but my opening angles could be even smaller, since its a project of 30 above grade floor levels with operable windows at every level. I did not fully understand your explanation. Which area is the one I could claim of the awning window as open? How will I calculate the reduced percentage if not? Are you suggesting that we have to measure the area of both "side" triangles formed when opening the window and that would account for the openable area? If not, please clarify. Thank you in advance.