Hi , I am working on a model in which the baseline is system 7 which means 1 system per floor, but the proposed system has different units serving one floor and they have different MERV filter ranging from 8 to 13, how to account for pressure adjustments in all the units since in the baseline we only have one system per floor and the zones in that system all have differnt MERV filters.
TIA
Rajat
3 thumbs up
December 13, 2023 - 10:47 am
Hi there Rajat,
I think I would do a weighted average of each system MERV ratings' pressure adustment with respect to the systems' delivered CFM.
Tyler Thumma
7GroupLEEDuser Expert
67 thumbs up
April 5, 2024 - 10:42 am
This is correct. However, note that MERV 8 filters do not qualify for a Baseline pressure drop adjustment.