NC-2009 WEp1:Water use reduction

Hotel guests

Hi, For an hotel. How can we count the guests?. Residents, FTE, or visitors/transients?. Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 06/23/2014 - 17:09

Hotel guests should generally be entered as residents. There is a LEED Interpretation out there which indicates how these should be calculated: http://www.usgbc.org/leed-interpretations?keys=100001771

Tue, 06/24/2014 - 06:20

This was as well covered in an addendum of November 2011: For hospitality projects, FTE and transient occupants are calculated per the typical methodology for the respective occupancy types. Hotel guests may be determined based on the number and size of units in the project. Generally, assume 1.5 occupants per guest room and multiply the resulting total by 60% (average hotel occupancy per AH&LA information) to determine the total number of hotel guests. Alternatively, occupants may be derived from actual historical occupancy numbers. Fixture use assumptions for hotel guests follow the fixture assumptions for residential occupants. Accordingly, lavatories located in guest rooms are considered to be private lavatories. Additionally, day use guests at the hotel should be included in the value for transient / visitor occupants. Per typical fixture use assumptions, this category of occupants assumes zero shower uses throughout the day. Example: 123-room hotelTotal Hotel Guests = 123*1.5 * 60%Total Hotel Guests = 111