Hello,

  Looking for additional clarification on on modeling HM doors on the perimeter of the building. The opaque doors are not labelled and therefore considering to use the following U-factor value from A7.1: "Insulated metal swinging doors, including fire-rated doors, insulated access hatches, and insulated smoke vents: 0.50"

1) Installer provided a certificate stating that with 1.75 inch thickness for the unlabelled HM doors with R-26 Rockwool insulation inserted under the hats and between the ribs of internal steel stiffeners, it's U-0.13. Is there any additional information should be asking them to support this claim, so I don't have to default to using the 0.50 U-factor per Appendix A7.1? 

2) There is a variety of HM door types from Corridors leading to MECH rooms and bathroom, that I intend to model. These HM doors have features such as "kick plates  with louvers". Is it necessary to model these interior doors considering temperature differential in these spaces?

Thank you in advance.