Adapting an historic building as a hotel use with all new HVAC, power, water and all systems but no thermal improvements to the exterior envelope. Does the baseline case stay the same for the envelope conditions and all energy savings must be achieved with the systems? It is not based on a comparable new hotel building, correct?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5867 thumbs up
October 9, 2018 - 10:02 am
Yes the baseline envelop would be modeled the same as the proposed. See Table G3.1-5 Baseline (f).