FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Heat Recovery in the Baseline Systems

For HVAC systems that consist of Fan Coil Units with Air Handling Units providing 100% Outside air - constant volume (based on the min ASHRAE 62.1 requirements) - Will the baseline systems require heat recovery as per ASHRAE 90.1 G3.1.2.10. All our AHU's specified have a design air capcity of greater than 2400 l/s. Not sure if this requirement applies to constant volume systems supplying min outdoor air ? can anyone provide guidance on this ?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/09/2016 - 15:36

The Proposed systems do not matter. Model the baseline systems according to Appendix G. See G3.1.1 which tells you how to zone the baseline HVAC system depending on the type of system. If any of the baseline systems require heat recovery according to G3.1.2.10 then include it in the baseline model.

Tue, 09/13/2016 - 22:32

Hi Marcus, Thanks for your comment. I am also wondering if the outdoor air modelled in both the baseline and proposed models should be the same OR is it the Minimum outdoor air quantity. I have a baseline auto sized model that has a much higher outdoor air quantity in CFM compared to the proposed model but the min. levels of the same. For info its not a VAV system. Can you please provide some guidnace ?

Wed, 09/14/2016 - 15:14

The quantity of OA should be identical in both models. Only exception is if the Proposed has demand controlled ventilation.

Thu, 09/15/2016 - 10:12

Another exception could be if in a model there is an economizer that increase the OA flow rate in order to minimize the cooling demand, correct?

Thu, 09/15/2016 - 13:10

Not really an exception per se, more like a different situation. The outside ventilation air should be identical in both models. The situation you describe would be bringing more OA into the building than is necessary for ventilation. If there is an economizer in one model and not the other the OA flow will vary when the economizer is operating but that is not to meet the ventilation requirements, it is to provide free cooling. So to be clear it is the minimum OA for ventilation that must be identical.