HAP version 4.5 is not capable of modeling hot water temperature supply temperature reset in the baseline case as required under ASHRAE 90.1-2007 Appendix G3.1.3.4 yet the software has been approved by LEED for energy modeling. Can anyone tell how to comply with this section of the appendix when using this software version?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
August 28, 2013 - 12:41 pm
I don't think you can do so. Technically the software you select to do your modeling for Appendix G (LEED) must be able to model the systems in your proposed and baseline buildings (G2.2). So if the baseline has a boiler you should not be using HAP unless you can figure out a way to include this strategy with a work around or through so kind of post-processing of the modeling results.