We have registered 2 buildings as a group project, both buildings are metered and we have the data for both buildings. We generated the energy portfolio for both buildings and there is a huge difference in the score between both buildings (98 and 72). However, we are aware that the credit submission will be separated for each building, but how the credit score is going to be calculated? Is it acceptable to submit the (72) scored building under the (Energy Star Rating) Option?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Trista Brown
Project DirectorWSP USA
456 thumbs up
September 5, 2018 - 4:31 pm
Hi - I think it makes sense to start by looking at the prerequisite requirements. The Group Approach guidance (from the Reference Guide) for the prerequisite states: "Submit separate documentation for each building; however, K-12 schools, hospitals, hotels, resorts, and resort properties with multiple structures, as defined by ENERGY STAR, may submit one ENERGY STAR score." Assuming that your project is not one of the property types called out, you'll need to document that each building individually meets the minimum ENERGY STAR score required by the prerequisite (75).
For the credit, the Group Approach guidance states "All buildings in the group may be documented as one." Not a lot of information, but you can get more by checking out the LEED Campus Guidance (https://www.usgbc.org/resources/leed-campus-guidance). Based on this resource, points for the credit are based on a square footage weighted average of the ENERGY STAR ratings for each building in the Group project (if they're the same ENERGY STAR space type). I recommend taking a look at that document for more info and an example.
So long story short, both buildings need to individually achieve an ENERGY STAR score of 75 or above in order to earn the prerequisite. From there, you can calculate the combined single ENERGY STAR score, and resulting LEED points, by using a square footage weighted average.